Cyclone - Xantrex pro Xm 1000 power inverter

Ottawa111

Member
On my 2015 Cyclone 4200, I noticed the fridge not working, the inverter stays on three broken red line. When we shut the power inverter on and off, a code EO5 flashes. When we disconnected the power to the unit it just stays three lines.
PS : is my inverter finished.
 
Last edited by a moderator:

Sowie

Well-known member
I too have a 4200. The error code I believe is the short circuit code. Did you try unplugging the fridge from the inverter to see if the code goes away? If it does you can reasonably assume the inverter is ok. You may have a pinched wire probably under the living room slide. If you still have the code with nothing plugged in then it’s the inverter.


Sent from my iPad using Tapatalk
 

danemayer

Well-known member
If you have the factory installed Magnum inverter, the manual says:

E05 Unit has sensed the input voltage is low and has initiated a warning alarm (@11.2 VDC).
Recharge the battery (to at least 11.8 VDC) as the unit will shut down shortly.
 