Our surge protector is hardwired. It keeps shutting off the power and the readout is showing the E4 code. If I shut down one ac or the other, the power stays on. While I am waiting for them to come and check the pedestal, I got to wondering what the normal readouts should be as far as each leg and how many amps the rig should use running both ac's. I am sure it is different for any rig, but is there a ballpark number? Its showing 20-23 amps with one ac going and around 42 with both. Also, I monitored our readout and on Leg one the voltage was dropping down to 103 and it is not up to 108. I am not sure if our rig is pulling to much power or not. I have also checked the end of the cord and it is not burnt nor is it hot IMO. It is a very hot day here.
Average on 1 AC - L-1 109 and 20 amps L-2 113 and 3amps 60 H
Average on 1 AC - L-1 109 and 20 amps L-2 113 and 3amps 60 H