Soft Breakers

CDN

B and B
Having issue in a park. 37 amp running tripping a 50 amp pedestal. Anyone else have issues like this?
 

Mattman

Well-known member
Is that both legs? One leg? Where did you take the measurement?
Does it trip when you do something or at random? Like air conditioner coming on?
Check your cord ends. Maybe one of your cords is bad. You'll never see the amparage draw inside if it's out in your cords.
Could be bad breaker. Can you try another pedistal?
 

CDN

B and B
The park breaker is tripping. The current is coming from the progressive EMS current transformer system.

The ambient temp was 90 degrees, I opened the lid on the pedstal to cool it down.

On phase one my coach loads, fridge main AC, ice maker, convertor etc 35 amps
Phase 2 Bedroom AC, Hot Water heater 32 amps, 37 at peak heat of the day

Voltage is 117 and 119 so not saving or brownout.

Checking with others they are blowing breakers as well.
 

Gary521

Well-known member
Try turning off the electric hot water heater and just run on propane. See if that keeps the breaker from tripping.
 

donr827

Well-known member
I had the same problem and the problem was the breaker in the pedestal . Ask the manager to check it out.
Don
 