Please do not try to do this. The reason you cannot find something like this in Walmart or on Amazon is if you cross-connect a 30A outlet to a 20A past the breakers, you do not "get" 50A. Even somebody did make a product like this, current would try to flow relatively equally from both outlets and you will just repeatedly trip the 15/20A's breaker by trying to draw 25A from it. More probably, you'd do something like drawing 42A which would work out to 21A per leg and still trip the smaller breaker, but cause it to run hot for awhile first, which isn't good for their lifetime.
The reason is that per Kirchhoff's Law, if you run X amps through a wire, if you now parallel that with a second wire, X/2 amps will now flow through both. It doesn't matter if there are breakers on those wires or not. Breakers don't SET current, they LIMIT it. It's still your device (AC, etc) that determines what the draw ends up being. So it won't help, and can lead to early breaker failure for the campground.
I tried to post a diagram but I get errors from the site when I add an attachment, sorry.
What TrailCreek said above is also true. My rant above is the best case. In the worst case, the 30A and 20A breakers are fed from opposite legs in the main breaker panel (sometimes, but erroneously, called "phases.") If that happens and you tie them together you're essentially shorting the main breaker for the campground! If you're lucky it will trip immediately, but it's going to be an exciting half-second before it does...