I am seriously looking at adding an Magnum Energy inverter/charger to our Cyclone 3100. I have spoken to 2 shops that recommend and install them. The first one recommended the MM1212, but I think the MS2812 would be a better option. One of the dealers had each little part called out with line item pricing (which I really like) but everything seemed to be generic. The other dealer recommended all Magnum stuff and it seemed to be self contained in one unit, with the normal add-ons. So, the list below is what I am looking at. Eventually, we will add a solar panel or two to help charge the battery bank.
MMP250-60S - Mini Magnum Panel (link)
MS2812 - Interter/Charger (link)
ME-ARC - Remote Control (link)
ME-AGS-N - Auto Gen Start (link)
ME-BMK - Battery Monitor (link)
GPL-6CT (qty 2) - Lifeline Batteries, 6v 300 amp hour (link)
I have read many other posts about making sure that the loads are leveled between L1 and L2. I will make sure that the installer does ensure this. I also assume, if I were to wire one of the a/c's to the sub panel and remove the 3-way toggle switch, then I should be able to run all 3 a/c's any way I want???
My biggest concern about the Mini Magnum Panel is what I read in the manual on Page 59:
Appendix B – Using the MMP in a Mobile Application
The MMP Series is designed and approved for use in residential or commercial applications. It has been tested and listed to UL 1741, 2nd Edition (inverters, converters and controllers for use in Independent Power Systems) for use in the US; and is also certified to CSA C22.2 No. 107.1-01 (General Use Power Supplies) for use in Canada. The AC input and output neutral connections in the MMP are combined and are bonded to the internal ground bar. The bond from neutral to ground can be removed as neutral is bonded to ground from the primary AC source.
In a mobile application, the standards for safely wiring RV, truck, and marine installations in the United States requires the neutral and safety ground to be connected at the AC source; whether it is a shorepower feed, an inverter, or a generator. This maximizes the possibility that a circuit breaker will activate if a hotwire-to-ground fault occurs. These standards also require that the AC neutral be connected to safety ground (often called a “bond”) in one, and only one, place at any time. The single bond is established in order to make the electrical panel’s neutral line safe, by connecting it to ground. Without this bond, the neutral can have up to 60 VAC with respect to ground.
Because the neutrals are combined, if the MMP is used in a mobile application, more than one neutral to ground bond may be established, which can cause current to circulate between the multiple neutral to ground connections. This can cause “ground-loop” currents, which can trip GFCI’s, cause an electrical shock hazard, and may be the reason for other annoying side effects.
MMP250-60S - Mini Magnum Panel (link)
MS2812 - Interter/Charger (link)
ME-ARC - Remote Control (link)
ME-AGS-N - Auto Gen Start (link)
ME-BMK - Battery Monitor (link)
GPL-6CT (qty 2) - Lifeline Batteries, 6v 300 amp hour (link)
I have read many other posts about making sure that the loads are leveled between L1 and L2. I will make sure that the installer does ensure this. I also assume, if I were to wire one of the a/c's to the sub panel and remove the 3-way toggle switch, then I should be able to run all 3 a/c's any way I want???
My biggest concern about the Mini Magnum Panel is what I read in the manual on Page 59:
Appendix B – Using the MMP in a Mobile Application
The MMP Series is designed and approved for use in residential or commercial applications. It has been tested and listed to UL 1741, 2nd Edition (inverters, converters and controllers for use in Independent Power Systems) for use in the US; and is also certified to CSA C22.2 No. 107.1-01 (General Use Power Supplies) for use in Canada. The AC input and output neutral connections in the MMP are combined and are bonded to the internal ground bar. The bond from neutral to ground can be removed as neutral is bonded to ground from the primary AC source.
In a mobile application, the standards for safely wiring RV, truck, and marine installations in the United States requires the neutral and safety ground to be connected at the AC source; whether it is a shorepower feed, an inverter, or a generator. This maximizes the possibility that a circuit breaker will activate if a hotwire-to-ground fault occurs. These standards also require that the AC neutral be connected to safety ground (often called a “bond”) in one, and only one, place at any time. The single bond is established in order to make the electrical panel’s neutral line safe, by connecting it to ground. Without this bond, the neutral can have up to 60 VAC with respect to ground.
Because the neutrals are combined, if the MMP is used in a mobile application, more than one neutral to ground bond may be established, which can cause current to circulate between the multiple neutral to ground connections. This can cause “ground-loop” currents, which can trip GFCI’s, cause an electrical shock hazard, and may be the reason for other annoying side effects.