danemayer
Well-known member
Woke up this morning with the furnace fan running continuously but not pushing heat.
Went outside and found that the burner was igniting, pushing hot air out the exhaust vent. After maybe 10 seconds the burner would shut off. Fan continued to run. After another 10 seconds or so the burner would ignite again. Then after 10 seconds shut off again. It just kept doing this.
Normally, if the burner tries to ignite but doesn't sense flame, the furnace shuts off and goes into lockout after 3 tries, also shutting down the blower until the thermostat is reset. This covers a low propane flow situation. If voltage is low, or blower airflow is poor (or restricted) the sail switch won't close, and ignition will not occur. 3 tries and lockout. So the fact that it wasn't going into lockout argues against a number of possible failures.
With the burner igniting and staying on for about 10 seconds, I think the flame sensor was satisfied that ignition had occurred.
That leaves the high-limit switch as the likely culprit. If it opened shortly after the burner ignited, it would shut off gas flow, but if the flame sensor had already signaled successful ignition, it wouldn't put the furnace into lockout. Blocking vents can cause this, but we don't have any vents blocked and airflow is pretty good at all vents.
Of course, shortly after I began investigating, the furnace began to operate normally. I didn't do anything to fix the problem.
Another possibility is a malfunction on the control board. Since the control board was replaced about 3 weeks ago, the board is certainly a suspect.
It'd be nice if these failures would happen during the day when the sun's out and it's 30 (F) outside, rather than in the middle of the night when it's -20 (F) or so.
I have a spare high-limit switch and a spare control board on hand. Just have to see how it goes.
Went outside and found that the burner was igniting, pushing hot air out the exhaust vent. After maybe 10 seconds the burner would shut off. Fan continued to run. After another 10 seconds or so the burner would ignite again. Then after 10 seconds shut off again. It just kept doing this.
Normally, if the burner tries to ignite but doesn't sense flame, the furnace shuts off and goes into lockout after 3 tries, also shutting down the blower until the thermostat is reset. This covers a low propane flow situation. If voltage is low, or blower airflow is poor (or restricted) the sail switch won't close, and ignition will not occur. 3 tries and lockout. So the fact that it wasn't going into lockout argues against a number of possible failures.
With the burner igniting and staying on for about 10 seconds, I think the flame sensor was satisfied that ignition had occurred.
That leaves the high-limit switch as the likely culprit. If it opened shortly after the burner ignited, it would shut off gas flow, but if the flame sensor had already signaled successful ignition, it wouldn't put the furnace into lockout. Blocking vents can cause this, but we don't have any vents blocked and airflow is pretty good at all vents.
Of course, shortly after I began investigating, the furnace began to operate normally. I didn't do anything to fix the problem.
Another possibility is a malfunction on the control board. Since the control board was replaced about 3 weeks ago, the board is certainly a suspect.
It'd be nice if these failures would happen during the day when the sun's out and it's 30 (F) outside, rather than in the middle of the night when it's -20 (F) or so.
I have a spare high-limit switch and a spare control board on hand. Just have to see how it goes.