Gfi problem?

apdurand

Member
Were new to this.. Shower Grey tank got full. Water came in under sink in bathroom. Now none of the outlets will work. No microwave, TV, fireplace. Gfi outlet in bathroom wont reset. Help please!
 

cookie

Administrator
Staff member
The microwave, TV and fireplace should not be protected by the GFI, so I would check all the breakers. Inside as well as the shore power pedestal.
Don't rely on a visual. Turn them off then on.

Peace
Dave
 

apdurand

Member
The microwave, TV and fireplace should not be protected by the GFI, so I would check all the breakers. Inside as well as the shore power pedestal.
Don't rely on a visual. Turn them off then on.

Peace
Dave
We did..and checked fuses. No power coming to outlets, checked with voltage tester
 

danemayer

Well-known member
If you have a 50 amp trailer, you may have lost 1 power leg. 1st place to check would be the power pedestal. If that checks out, make sure the shore power cord is seated and locked at the trailer end.
 

Roller4tan

Well-known member
Obviously, water and electricity don't mix. You may have to look in the basement area behind the panels for any signs of water. GFIs wont reset if there is no power to them. If the water got to the back side of your breaker panel it could have shorted wiring in the area.
 

apdurand

Member
Obviously, water and electricity don't mix. You may have to look in the basement area behind the panels for any signs of water. GFIs wont reset if there is no power to them. If the water got to the back side of your breaker panel it could have shorted wiring in the area.
Right.. Have husband check that next. Thank you
 

wdk450

Well-known member
Just to verify things: 1. You have a 50 amp wired trailer? 2. You are connected to a 50 amp shorepower outlet? If connected to a 30 amp shorepower outlet, have you checked (swapped) your 50 to 30 amp adapter in the power feed line?

If indeed you have a 50 amp wired trailer connected to a 50 amp shorepower cord, I would take the metal surround off of your inside breaker panel, and do some voltage measurements with your voltage tester. Nearest the double master breaker you will see the shorepower cable with 4 large wires coming out of it. The green wire is ground and should be connected to the ground buss, the white wire is neutral, and should be connected to the common neutral return buss, the red and black wires are the 2 hot 120 volt feeds which should be connected to the double mains circuit breaker. Check the voltage where these wires connect to the mains. There should be 120 VAC to neutral/ground at both of these connection points. This double mains breaker can have problems in connecting to the 2 buss rails in the breaker box causing 1/2 of your power to be missing. On my breaker box every other branch breaker is on a common phase feed, so checking the voltage out of the branch breakers at the wire feed connection points is a good way to make sure that both phases are getting through the mains breakers to the buss rails and the branch breakers.

Making these measurements should give you a better idea of what is going wrong, at least upstream (before) or downstream (after) the breaker panel. Be safe when making these measurements, and shut off the power while removing/replacing the breaker box faceplate.
 

apdurand

Member
So..an update. Most outlets are working now. The 2 on the island, the gfi and the one outside by the basement arent working still.
 

wdk450

Well-known member
Island, GFI, and outside all should be on the GFI circuit. Can the GFI outlet be reset? Does the GFI outlet have an indicator LED to show if it is passing power? You can pull out the GFI outlet and measure for power coming in/ power going out. GFI outlets aren't that expensive, and pretty easy to replace. Just turn off the power when working around it.
 