Hi Winn369,
Welcome to the Heartland Owners Forum.
I moved your post to its own thread in the 12V DC sub-forum.
If I understand your problem description:
- On shore power, with no battery installed, the furnace operation was intermittent.
- Still on shore power, you installed a battery and the furnace ran ok for a while, but then stopped.
- After you charged the battery (presumably with a standalone battery charger), the furnace ran again, for a while.
- When the furnace does run, while it's running, the refrigerator stops working, but resumes working after the furnace is off
- And your (interior?) 12V DC lights flash.
Before installing a battery, if you had the problem with the furnace, the refrigerator, and the lights, I would think the Power Converter is not putting out normal voltage. An easy way to check this while on shore power, while you're experiencing failure symptoms, is to press the test button on your Tank Monitor Panel. In addition to showing holding tank water levels, it also shows the voltage level of the 12V system. On shore power, you should always see 4 lights because it's reading the Power Converter output. If you see 3 or 2 lights, that would mean the voltage out of the Power Converter is low. One possible confusion factor would be if the battery is fully charged, you might see 4 lights for a while, then 3, then perhaps less as the battery discharges.
The Power Converter normally outputs 13.2V DC or higher if measured with a voltmeter, which you can do at the fuse box.
We have 2 owner-written guide you may find helpful. The 12V Block Diagram and Diagnostic Guide is
here, and the Electrical User Guide is
here.