I believe the OP was all about getting 50A to run two AC's.
I couldn't find a EU7000 manual but the answers to your questions are probably in the similar EU6500 manual.
http://cdn.powerequipment.honda.com/pe/pdf/manuals/31Z25600.pdf
On page 10 the 30A prong on the right is a 4 prong outlet that per page 14 can be set to 120V or 240V.
If you set it to 120V and use a four prong generator adapter like the one below you should be OK to use a 30A/30A to 50A Y adapter. 30A 120V to each side.
http://www.electricgeneratordepot.c...&CAGPSPN=pla&gclid=CIrrhsbO8L8CFVJo7AodeSQAsQ
If you use a Y adapter and put 30A 120V to one side and 30A 240V to the other side, that's a problem. But that should not be possible with the above adapter. Bill's right with a 4 prong 30A plug you have a total of 240V spilt to 120V on each side of your panel, but still only 30A, 240V on one side would be wrong.
Just to make sure you can run the outlet test at Bill's link...
http://www.myrv.us/electric/
Gentlemen?
The OP is me, I was the one questioning you on that. Correct that I want to pull 50amp to run 2 AC units. I feel like a MAJOR horses-azz as I have been leading everyone astray with incorrect info. I thought both receptacles were the same 30AMP 3-plug outlets. I made an honest mistake by hardly looking at the unit. I have only used it a couple times. The receptacle on the right is in fact 4-prong. So correct, with the right adapter I should be able to hook directly with a 4-prong twist into my 50AMP cord that Branson4020 suggested. http://www.homedepot.com/p/Rodale-1...ale-Adapter-G30AM450AF/202669079?N=5yc1vZc4mv
I did read the info from wdk450 on the 120/240 page, but I don't understand all of it. Should the selector be on the 120 setting, or 240 setting? I would say if I want more than 30AMP I need to be on 240 correct?