danemayer
Well-known member
I am down by Corpus Christi, and last night almost froze to death, no electricity and dead batteries and then about noon today power is turned back on and the heater started right up. Only problem is the thermostat is set at 75 degrees, it won't change up or down nor can you cut it off. But it is recycling on and off about every 4.5 to 5 minutes. I called a mobile repair guy and he had me remove the unit from the wall and remove the phone jack plug for a couple of minutes and put it back. No improvement, but in trying to get something to happen it showed an E1 error code which the book says "is a loss of communication between the CCC 2 Dometic thermostat and an individual system power module board". It doesn't say if the problem is in the thermostat or the module board. I only have one zone for this thermostat so it is Zone 1. The repair guy said he would get two white thermostats, one for AC and one for Heat which doesn't excite me. In looking at Amazon, I find they have what looks like the same thing. Has anyone had a similar problem and plugged the phone jack into a new thermostat and it worked? Also, does anyone know if there is a way to clear the error code? A friend said that if you could do that it might work. Thanks for any suggestions.
George, an E1 code is often a bad/dirty/corroded connection at the air condition - on top of the rig. It's pretty rare to have a bad thermostat.