I need to clarify my earlier comments - I said I used the Class T to protect my inverter; this is partially correct. I should have stated I used the Class T to protect my inverter
installation - including the wires. In the electrical community experts correctly state the fuse is to protect the wiring. My Xantrex and batteries are capable of high short circuit amperage - the fast acting, high AIC of the Class T is needed to protect the installation - the probable mode of failure in a short circuit case, would be that my wires (2/0) would melt and possible cause a fire.
I used a circuit sizing program similar to this -
BlueSea Circuit Wizard - to calculate the wire size, fuse size the 300A, 2/0 gauge, 10ft circuit length (5 ft each way, positive cable and negative cable). I chose to keep voltage drop to less than 2%.
Hope this helps, and does not add more confusion. Apologies on the earlier lack of clarity.
Brian