I'll make my ASSumption on what happened...
Previous owner had the #6 Main CB either kick out and didn't know about a reset button on it, or the CB just gave up the ghost...so he/she had a loss of 12V charging and supply. Then they tilted top of #6 to the right for clearance and installed main feed wire onto #5 CB to bypass #6. The jumper was to share #4 CB for the modification.
If it were mine, I would do some testing first....but take the jumper from #4 and throw away. Straighten top wire on #4 to get it farther away from CB #5. Take that wire that is now under the jumper on top lug of #5 and put it on top of #6. Leave the back wire on top of #5.
That looks like it would be back to factory configuration to me.
Now, chances are great that #6 CB would need to be reset or replaced.
LBR, you hit the nail on the head. The manual reset breaker (#6) had been tripped, and I reset it. That's probably why someone had moved the wires around. Here's what all the original 6 AWG wires were (this is my original photo, just annotated):
The extra 6 AWG wire turned out to be the generator starter. So the fuse box/converter, hydraulic pump and generator starter were all sharing a pair of breakers wired in parallel (total 80A or 100A).
And here's the buss bar after I moved things to what I think are their proper places:
The type III (manual reset) breaker (#6) was passing current once I reset it. It may be weak, but I won't know for sure until when and if it fails. Although the wire to that breaker is labeled Fuse Box/Converter, in reality the converter is not connected, because we replaced it with a separately-fused inverter/charger when we put in our solar power system. For now at least, the breaker is working properly.
I also found that the crimp on the line to the fuse box/converter was loose, which might explain some of the problems I'd seen with loss of 12V power to the fuse box at times. I re-crimped it.
I've ordered an 80A breaker to replace the 50A now in use for the hydraulic pump. I've also ordered a 50A type III breaker and a 50A type I (auto reset) breaker to keep as spares in case one of the existing breakers fails, which I almost expect to happen.
Thanks everyone for your help!
- - - Updated - - -
Do you know where the output of the solar control connects to the battery? Is it possible the third thick wire is from the solar controller.
I'd hazard a guess that someone installed the jumper on the theory that they could increase current flow by using two breakers in parallel - possibly an attempt to fix the hydraulic pump starting and stopping.
If you haven't read it, take a look at the
Hydraulic Slide Out Starts and Stops user guide.
Dan, the solar controller output is connected directly to the battery bank through a separate fuse installed near the controller. The third 6 gauge wire turned out to be the generator starter circuit.
And thanks for the pointer to that user guide. I read it when I started researching the problem in the first place, and that's how I ended up trying to untangle all the wires on the buss bar so I could figure out which breaker to replace.
I have a feeling that the shop that "fixed" our hydraulic slide out stopping problem shortly after we got our rig--before I knew any better--was responsible for the rewiring and jumper mess. They told me they repaired a weak breaker, and I assumed that meant they'd replaced it, not just wired around it. But I guess not.
- - - Updated - - -
One last question: should the breaker on the generator start circuit be 50A or 30A? I'm guessing 50A based on the size of the wire.