6.7LMegaCab
Well-known member
After going back and forth on deciding a route to take with a new converter and getting an inverter, I decided to stick with PD. At this time, we don’t need a whole lot of AC power when the Gen or Shore power is disconnected, thus the reason for the 1000W inverter.
With that in mind, I decided to get the 1000W inverter from PD. Since it has a built in transfer switch, I’m slightly confused on how to wire it in based on the wiring diagram from the install guide.
This is my current setup:
Cummins/Onan 5500W GenSet
Shore Connection
PD52DCS 50A Auto Transfer Switch
PD9260 Converter (to replace the WFCO 9855)
WFCO 8930/50 AC/DC Distribution Center
4x US Battery US 2200 XC2 6V 232AH Batteries
Ideally, I’d like to hardwire the Inverter to one side of the Distribution Center, but still have that side operating on shore or gen power.
Would it be appropriate to take one side of the hots (red or black) from the PD52 transfer switch and wire it to the AC-In of the inverter and run the same size wire from the AC-Out to one of the 50A main breakers? We will not be running the Air Conditioner while on battery.
Here is a diagram I drew up of what I think it would look like:
I appreciate any feedback to make this right, the first time.
Also, any recommendations on a DC fuse or circuit breaker for the battery side is greatly appreciated.
Actually, I just read the install instructions again...there is a 15A breaker built in, so I obviously can’t connect directly from the PD52 Transfer Switch to the breaker box. So the diagram above will not be appropriate, any recommendations to wire it would be greatly appreciated. I guess what doesn’t make sense is how to provide power to one side of the AC bus bar while on the Inverter and still allow Gen or Shore power on that side.
The install guide shows all three connected on one side of the distribution center.
Thank you!
-Josh
With that in mind, I decided to get the 1000W inverter from PD. Since it has a built in transfer switch, I’m slightly confused on how to wire it in based on the wiring diagram from the install guide.
This is my current setup:
Cummins/Onan 5500W GenSet
Shore Connection
PD52DCS 50A Auto Transfer Switch
PD9260 Converter (to replace the WFCO 9855)
WFCO 8930/50 AC/DC Distribution Center
4x US Battery US 2200 XC2 6V 232AH Batteries
Ideally, I’d like to hardwire the Inverter to one side of the Distribution Center, but still have that side operating on shore or gen power.
Would it be appropriate to take one side of the hots (red or black) from the PD52 transfer switch and wire it to the AC-In of the inverter and run the same size wire from the AC-Out to one of the 50A main breakers? We will not be running the Air Conditioner while on battery.
Here is a diagram I drew up of what I think it would look like:
I appreciate any feedback to make this right, the first time.
Also, any recommendations on a DC fuse or circuit breaker for the battery side is greatly appreciated.
Actually, I just read the install instructions again...there is a 15A breaker built in, so I obviously can’t connect directly from the PD52 Transfer Switch to the breaker box. So the diagram above will not be appropriate, any recommendations to wire it would be greatly appreciated. I guess what doesn’t make sense is how to provide power to one side of the AC bus bar while on the Inverter and still allow Gen or Shore power on that side.
The install guide shows all three connected on one side of the distribution center.
Thank you!
-Josh
Last edited: