I believe the limit switch is on the inside as it detects an overtemp condition. It's in series with the sail switch as shown in the wiring diagram. Note there is an alternate path for the board to get power to the blower, independent of the limit and sail switches.
I've attached a troubleshooting flowchart.
View attachment 66604
Dan, thank you! This is the chart I've been trying to follow from the installation manual that came with the rig. It seems like something is missing from it as the motor has 3 or 4 wires coming out of it...I'm baffled. I'll look at it again in the morning.
Possible broken wire? I don't know your system, but have extensive HVAC background. If your furnace uses a separate thermostat, (I have a 1 thermostat for heat/AC, and furnace) than verify voltage to the thermostat, and voltage out of the thermostat when calling for heat. if voltage is present at both in and outs of the thermostat, then you need to follow the out voltage wire that goes to the input of the furnace board.
If you are certain of the voltage input wires on the furnace board, you can remove those input wires, and connect a 12v source to them, IE: battery like you did with the fan. That should make the board react as if the thermostat is sending voltage to it.
The furnace is connected via the Dometic proprietary AC thermostat. So when you set it to heat, you get an audible click from a relay on the AC control board, and then an audible click from the furnace - but I don't think the click is coming from the control board...hard to tell though.
From what I can find, there are only 4 wires coming from the electrical cabinet area that go to the furnace. Two white wires, which come from the ceiling AC unit and are the Furnace Y3 and Y4 and drop behind the cabinet and go across the other side via the basement to the furnace. The other two wires are a red and black wire that looks like it is coming from the bottom of the cabinet, possibly from the fuse panel...hard to tell. Both white wires have +12V when heat is called for. Y4 has a constant +12V regardless of whether heat is called for or t-stat is off. The red wire has +12V and the black wire is confirmed good continuity to ground.
I was trying to get the red "Power" wire off of the board to isolate that and connect a battery directly to it, to see what it does, but that spade connector wouldn't release. I'll try again tomorrow and attempt your recommendations.
What you posted in this sentence seems to indicate that the wiring from the 12 volt fusepanel to the furnace power input is good: "Is there some other hidden fuse or CB somewhere that is between the combo 120 main breaker/ 12V fuse panel that controls power to the furnace? There is a fuse for the furnace on that main panel and when heat is called for and pull the fuse, the LED lights up, so I know that is good."
Change that fuse just for the heck of it.
Did I understand correctly that you measured with a voltmeter where the power is supposed to come in to the furnace control board, and got 0 volts instead of 12 volts DC? On perplexing problems like this you may need to run an external test wire from a good 12 volt dc source directly to that circuit board 12 volt dc power input point, then see if it works.
On edit (after viewing the schematic) : Incoming power is +12 vdc on a red wire and -12vdc (ground) on the yellow wire. Are BOTH connected correctly?
Luckily, I got a lot of spare fuses...I'll change it tomorrow.
Yes you did read correctly. If I can get the red power wire off (see below), I'll hook up a separate battery to see if this gets the circuit to work.
If I recall, the connector with the 4 wires on it that connects to the PCB has the red and yellow wires on it (along with brown and blue wires)...there is zero voltage on either of them (I'll double-check again tomorrow though). The Red wire with a female spade connector is connected to a double male spade soldered to the board, the other male has a blue thermostat wire that goes to an on/off switch just to the left of the board - YES the switch is on...in fact, never knew it existed until this unit stopped working. This red wire is what the schematic shows as the POWER wire for the board, which, according to the schematic, it appears that is the first point for the blower motor to kick on to get the whole circuit working. If the power wire would work, it should send the +12V and -12V to the red and yellow wires you mentioned...again, if I'm reading the schematic correctly. I read the schematic again - I don't recall seeing another yellow wire anywhere (the yellow wire that has the -12VDC annotated next to it). It might be part of the wires I can't get to unless I pull the furnace.
There is another red wire on a separate male spade soldered to the board right next to the other two wires. This goes directly to the blower motor. I disconnected that wire and connected a separate battery to it which immediately powered up the blower.
I have never touched this system and for the 4 years we've owned it, the furnace has always worked...until this past week...and only worked for one night. So I can assume they are all hooked up correctly. I'll dig some more to find that other yellow wire.
Thanks again for all the replies folks! This is helping....I'm all ears for other ideas. I'll be back at it tomorrow.