We pulled into our site yesterday and plugged the Progressive EMS into the 50 amp receptacle and plugged the shore power cord into the EMS. Turned the breaker on and went on with setup. A few minutes later I went inside and was surprised there was no power yet.
Went out and looked at the EMS - blank display. Turned the breaker off and on. L1 = 123V. L2 = 123V. Waited 2 or 3 minutes inside. Still no power. Went outside and found the EMS display was blank with an occasional flash of lights.
Grabbed an adpater and plugged the EMS into the 30 amp receptacle. Everything worked. Called the office and asked them to send maintenance out.
The maintenance guy decided the problem was in my Progressive EMS and suggested running a test by plugging the shore power cord into the 50 amp receptacle to see if everything worked. I declined. I demonstrated the EMS working in the 30 amp receptacle, and in the 50 amp receptacle in the next site (without shore power cord attached). Then showed in failing in our site's 50 amp receptacle. He called for reinforcements.
2nd maintenance guy showed up with a volt meter and pronounced everything ok after a routine check. I suggested that maybe he should take a closer look at the neutral connection. Turns out the neutral connections were all loose at the neutral buss bar inside the pedestal. Plugged the EMS in and it worked for nearly 2 minutes before shutting down again.
Maintenance complained that he had just replaced the receptacle on this pedestal 2 days earlier. I suggested he replace it again. He hemmed and hawed but after a couple of minutes went to get another receptacle. Also brought a new 50 amp breaker. Replaced both. Bingo! Everything works.
My guess? The loose neutral wire at the buss bar was probably detected by the EMS without triggering an error code on the EMS. The problem on the neutral buss probably caused heat damage to the neutral connection at the receptacle.
What would have happened if I had plugged in without an EMS? Pretty good chance that voltage on one leg would have gone high and the other low. Good possibility of damage to motors or electronics in the trailer.
If you don't have an EMS, get one.