Those trying to run all 3 AC units would be wise to check your loads at the breaker panel.
My panel was not balanced well at all, main AC, converter, hot water heater and all the outlets were on one leg (which included the coffee maker, micro and W/D).
Cyclones are equipped with 80 amp converters, so it is not unusual for me to see 12 amps or more at times, with nothing else on.
I don't see why all three AC's could not run at the same time - if you balance the panel.
My guess is they are set to only run any 2 of 3 units because of either RIVA codes - or more likely, because the available generators are only 5500 watts. Two circuits at 30 amps each, and that is under ideal conditions (temperature, altitude etc).
Park supply voltage is something we have to concern ourselves with as well.
"If" our trailer had the 3 AC units I would balance my 100 amp (50 x 2 = 12,000 watts) panel that:
a) indeed balances it
b) balance it based on our use.
I would then have some simple to use method of isolating one of the three AC's when using the genny.
Our home generator has load shedding built into the the main control unit. It sheds the AC simply be disconnecting the T-stat call for the compressor.
So, perhaps a simple mini on/off switch on the T-stat to the compressor circuit will work.
Onan
Ambient conditions for
rated power output with muffler and RV enclosure, per ISO 8528-1:-
Temperature: 77° F (25° C)
Altitude: 500 ft (152.4 m), (99 kPa dry)
Typical power output change based on ambient conditions:
Temperature: Power output decreases 1% for every 10° F (5.5° C) increase
Altitude: Power output decreases 3.5% for every 1000 ft (305 m) increaseRatings represent minimums. Actual performance may be significantly higher based on installation and operatingconditions.
The gasoline versions are more efficient then the LP's. So non toy hauler types have an additional loss of power available.
Using the above info, "if" we were camping in the Smoky Mountains back in August 2008 during the drought and heat wave, our 45.8 amp actual output Onan 5500, at a temperature of 106 degrees and elevation of 6500', would have had an output of only 35.9 amps.