klindgren
Retired Virginia Chapter Leaders
Keith,
Is the problem bidirectional? That is, does it matter which side/tank it's switching to when the failure occurs. For example, if it always fails when switching to the doorside tank, you may have a problem with the pigtail or regulator on that side, or with the crossover hose.
If it always fails when switching to the off-doorside tank, you may have a bad pigtail on that side.
Dan, I am now convinced the problem is uni-directional. When the regulator is on the off door tank, the systems works as it should, switching tanks without a problem. However, when the system is on the door side tank, it will not switch tanks. I have to go outside and manually switch the tanks, then restart the furnace. There is a regulator on the door-side tank (not the auto-switching kind). I wonder if that could be the problem.