Update, problems fixed,Rear AC Problems
None Original problem post is below.
The tech was out Friday and fixed the AC unit.
Problem 1 . Was the leaking inside. Fix, The sealent (using this term loosly) was not keeping the hot air from mixing with the cold air, and I could see light lookin up through the vent. The tech reinstalled the sealent foam material and the used foil tape to seal everything up.
Problem 2. AIr conditioner compressor cycle off/on when themostat was off . Fix. was replacing the control circuit board in the AC unit. Tech thought that maybe the water leaked onto the board and shorted it out.
It ran all weekend and no drips and shut off when it was suppose to. Also the air through the ceiling vents flows at a higher vilosity than before.
We have owned our new Bighorn 3670RL for about 2 weeks now, and have been having Probles with the rear 15K unit.
The dealer is coming out Friday to look at it, but since this is my first 15K unit with a wall mounted thermostat control, I have a few questions.
Here's the problems
Water dripping inside. Thermostat set to AC, auto (or on either way it drips), fan HI, and about 75 degrees. Drain hole is clean looking from outside unit. Also when raining NO drips from unit, so seal should be ok.
They say this unit has a freeze sensor, that may have come loose.
Now when I turn the thermostat to the off position, fan to auto and slide the temp all the way up, the unit will still cycle on and off. I finnally shut the breaker off to keep the unit from running.
The front AC a 13k unit was installed at dealer, is working great.
now the questions
What would cause the the unit to cycle off/on with thermostat set to off? Is it the AC unit or the thermostat that could be causing the problem?
None Original problem post is below.
The tech was out Friday and fixed the AC unit.
Problem 1 . Was the leaking inside. Fix, The sealent (using this term loosly) was not keeping the hot air from mixing with the cold air, and I could see light lookin up through the vent. The tech reinstalled the sealent foam material and the used foil tape to seal everything up.
Problem 2. AIr conditioner compressor cycle off/on when themostat was off . Fix. was replacing the control circuit board in the AC unit. Tech thought that maybe the water leaked onto the board and shorted it out.
It ran all weekend and no drips and shut off when it was suppose to. Also the air through the ceiling vents flows at a higher vilosity than before.
We have owned our new Bighorn 3670RL for about 2 weeks now, and have been having Probles with the rear 15K unit.
The dealer is coming out Friday to look at it, but since this is my first 15K unit with a wall mounted thermostat control, I have a few questions.
Here's the problems
Water dripping inside. Thermostat set to AC, auto (or on either way it drips), fan HI, and about 75 degrees. Drain hole is clean looking from outside unit. Also when raining NO drips from unit, so seal should be ok.
They say this unit has a freeze sensor, that may have come loose.
Now when I turn the thermostat to the off position, fan to auto and slide the temp all the way up, the unit will still cycle on and off. I finnally shut the breaker off to keep the unit from running.
The front AC a 13k unit was installed at dealer, is working great.
now the questions
What would cause the the unit to cycle off/on with thermostat set to off? Is it the AC unit or the thermostat that could be causing the problem?
Last edited: