A 10V drop is signalling a problem.
Is your EMS before the transfer switch? If so, the voltage drop is in your cord reel, or the receptacle or house. If the EMS is after the transfer switch, it could be the transfer switch. Pitted contacts, a loose wire, or failing contactors are all possible.
Don't put too much faith in the electrician. A license doesn't keep them from making mistakes. Ask my generator how it felt when the electrician miswired the transfer switch at the house.
Can the 50 amp box cover be removed so you can check for a voltage drop there when the 2nd AC kicks in?
One other thought: are the 2 A/C units on different power legs. Turn on A/C 1 and look at the EMS monitor to see which leg is carrying the load. Turn it off and turn on A/C 2 and see if it's on the other leg. They should be on different legs. Even so, if on the same leg, that would only possibly cause a drop if you're around 50 amps on 1 leg, meaning other things would be sharing the same power leg.
We're going to see if we have a drop at the 50 amp plug when AC is on in the morning... exhausted right now from the heat. We checked each AC separately and they are on separate legs. The EMS is after the transfer switch because of the generator. We just replaced the transfer switch last July as we had a loose connection and burned a lug on the generator side...every single connection was checked and tightened in the rig.
This is the most baffling thing we've ever dealt with