> I do have the electrical drawing and it shows the start cap. hooked into the run cap. with just two wires that are simply clipped in place.
> It appears all that needs be done is unclip wires remove old cap. attach new one to the same clips on the running cap. that the oem was
> attached. Am I right?
> PS- I called Supco Tech help today and they said to piggyback the supco unit to the oem capacitor, ie, don't remove the original capacitor.
> It makes no difference which terminal the black wires on the supco are clipped.
> My unit is a Carrier Air5 . Hope this helps someone.
If one does not have any AC starting problem when using "normal" AC power, and all one is trying to do is reduce startup load for use on 120 Volt 15 Amp shore power or when on generator power, then here is my two cents for a 13,500 BTU AC:
1. If you are going to leave the original PTCR and Starting Cap in place and they are good, then I would use a SPP6, this is what SUPCO technical support recommends. it wires in parallel with the current Start Cap + PTCR on the same run cap terminals. SUPCO says the SPP6 will work, that the SPP6E will also work but its extra features are not needed.
2. SUPCO does not recommend taking out the original starting capacitor components! I had personally done this on my Dometic 13,500 2010 manufacturing vintage AC unit, removing them and replacing them with the SPP6E. Amazingly, it actually will start and run reliably now even with the Edge M21 plugged into a 120 volt 15 amp breaker fed outlet and 100 foot 14 gauge extension cord. FYI, once running it draws 13.5 amps, 1400 watts from the 120 volt outlet.