Last time I looked in the power pedestal at my site, the 50/30/20 amp circuit breakers plug into a buss that receives power from the park's power distribution system. There's no master breaker at the pedestal that cuts all power to the pedestal. Just breakers for each receptacle.
There are 2 power legs coming into the pedestal; each carrying 50 amps at 120V. Hopefully the 30 amp breaker is tied to 1 power leg and the 20 amp to the other. But, I haven't inspected the buss and breakers and wiring to see if that's the case. It's just my assumption. Worst case, one 50 amp leg is also carrying the additional 30 and 20 receptacles.
If I run everything inside the coach at the same time, and max out both 50 amp legs, I'd be using the full capacity of the 50 amp park pedestal. Another way of saying that is if your Power Control System starts shedding loads, you're running at or near the capacity of the pedestal.
If I then plug a separate 15 amp load into either the 30 amp receptacle, or the 20 amp receptacle, the total load on the pedestal will exceed it's capability. One leg will be trying to draw 65 amps from the park distribution system.
That leads to a question about the wiring from the park distribution system to the pedestal. Will the wire be ok with a 65 amp load? Since I don't have any knowledge of that wiring, I don't know. Maybe it's ok or maybe it'll get overheated.
Is there a 50 amp master breaker at the park distribution end of the wire? Will it trip if I try to draw 65 amps? Another unknown. But if it does trip, I'd guess I'll be without power until the park can get their electrician to investigate.
My advice is to rely on the Power Control System. If you want more air conditioning, have a pizza delivered so you don't have to run the cooktop or convection/microwave. Or dry your clothes later.