Its a Progressive dynamics power center Model PD55K000. If I am understanding you correctly, if the breakers are labeled correctly, what I could do is get a dual 20 amp and a dual 15 amp, run the wires accordingly and should then have an AC on each leg. If that is the case I can handle that just fine. My wife is on a ZOOM call so I cannot turn anything off just yet in case things are not labeled correctly. I appreciate your assistance!!So we have to dig a little deeper.
Can't tell from the picture how the back plane of the panel is arranged. On my Sundance, the 50 breakers are in the middle and L1 and L2 on the back plane are to the left and right of the 50's respectively. Your picture would suggest that each twin breakers sets alternate between L1 and L2. If that's so, then "as marked" each AC is on a separate leg. That is not consistent with your measurement.
This then adds another question. Are the breakers marked correctly? It's not that unusual for the factory to mark them incorrectly. So the first thing I would do is turn on each ac separately and then turn off the breaker associated with it to verify they are in fact marked correctly. Next step would depend on what you find.
Do you have a brand and model number of the panel in order to look it up? That would help especially if you are uncomfortable working on this.